Post by Steve the Gas »

I'm against the clock today, if your valve has a sliding arm/slider on it, then set it to the manual position. Ask for heat via the thermostat and it should carry on working.
If this works then the valve is kaput/or just the head or it's wired up wrong. )t'


Does that any make sense to you??
User avatar
paddy graham
Legendary Laner
Posts: 2522
Joined: 13 Oct 2010, 15:58
Location: Co.Sligo,Eire

Re: Paddys' Boiler

Post by paddy graham »

Thanks a lot Steve,I will check that when I,m dressed )t'
When Irish eyes are smiling,they are usually up to mischief.
Steve the Gas

Re: Paddys' Boiler

Post by Steve the Gas »

My other thort is the pump, is it actually turning?
You can check by removing the big silver screw in the centre and turn the shaft with a screwdriver. A dribble of water may come out but that's all, then switch on so you can see it turning. Has the system and boiler been bled of air?
User avatar
paddy graham
Legendary Laner
Posts: 2522
Joined: 13 Oct 2010, 15:58
Location: Co.Sligo,Eire

Re: Paddys' Boiler

Post by paddy graham »

Steve, the man that put the stove in for me just called,I tried to explaine what you said but no,no he said,so I showed him your posts,he went back and had another look.The pr-t had not turned the one valve back on.All working fine now,thank you very much. :-D )t'
When Irish eyes are smiling,they are usually up to mischief.
Steve the Gas

Re: Paddys' Boiler

Post by Steve the Gas »